EXECUTIVE SUMMARY
Context
How to Estimate Arc Flash Incident Energy When You Do Not Have a Proper Arc Flash Study
Different approaches exist for determining the correct amount of PPE to protect workers from arc flash. In the absence of an arc flash study, workers may turn to NFPA 70E tables 130.7 (c) (15) (a).
The table, however, may be difficult to apply to a specific task or situation and may be very conservative, or not conservative enough. Graphical approaches like energy boundary graphs can be useful because they incorporate fault current variance and do not require the need to know the exact performance of an overcurrent protective device at a specific value of arcing current.
Key Takeaways
Short circuit studies and almost all electrical system studies are biased conservatively—impedances are estimated low, while sources and short circuit currents tend to be estimated high. Short circuit studies ensure that all equipment ratings are high enough to handle potential worst case short circuit currents. If a high short circuit current event occurs, there could be serious consequences should equipment not be adequately rated.
Many of the values and inputs used for these calculations are never known exactly. If an error is conservative or within a margin that other factors account for, it’s okay.
The IEEE 1584-2018 model is conservative with respect to Ei, but Valdes believes it may not be conservative with respect to low Ia. IEEE 1584-2018 may not truly account for how low Ia can be, because it ignores factors excluded from the original test data. Some variance in Ia can have a significant impact on Ei.
First, arcing current (Ia)
Second, Incident Energy (Ei)
A constant energy boundary (CEB) shows graphically how a protection system performs against a specific PPE performance target and range of arcing current. The CEB in the image below shows 480V, 18” D, 25mm G, in a standard box up to 100kA Ibf.
If Ibf is not a well-known variable, then Ia is even less so. Both the circuit breaker and fuse are “steeper” than the CEB. As a result, low Ia can result in higher energy than high Ia. This is counterintuitive. At high Ia, both the circuit breaker and fuse may be good enough. Fuse size matters whether it’s current limiting or not, and circuit breaker size, type, and settings matter.
If you have an IEEE 1584-2002 study but not a 2018 study:
NFPA 70E takes a task-based approach to hazard risk analysis which has two steps:
Different Iarc and Ei
NFPA 70E Tables
Equipment descriptions include OCPD type or size and have equipment descriptions that don’t follow applicable standards. Switchgear, for example, doesn’t have fused switches.
Most table entries can result in higher energy if arcing current is low or, worse, if the arcing current is low through the OCPD but not low at the arcing point, which may be the case with sources in parallel or significant motor contribution.
Rather than relying on NFPA 70E, a better approach may be to check with someone who understands arc flash calculations.
Shortcomings with NFPA 70E Table 130.7(C)(15)(a)
Focuses on a “maximum” Ibf and what the OCPD does at fault current.
The constant energy line is another way to determine the correct level of PPE.
With this graphical method, you determine what you need to know to select PPE, consider variance in the fault current, and use variables that you have access to.
Determining PPE with a Constant Energy Line